ron2
Posted : 7/25/2008 8:32:49 PM
rwbeagles
As mentioned prior we got a new AC unit recently. It's been kickin butt and working great...BUT the inspector for the city came by per usual and said "breaker is too big...needs to be switched out". We had the installers do so...and now I swear it's not working nearly as well.
Now I cannot at all figure out why the two would be connected...and they might not be...but does anyone know a reason why it might be related to the breaker switching out?
Breaker is on, compressor runs, thermostat runs..no breaker trip...air blows out...but it's FAR from cool or even cold like it was. DH is calling the co. back out to looky but I wondered....
Which breaker? You have an ac disconnect outside that looks like a breaker and is actually a specific type, usually an HACR. It's designed to put up with the current spike on start-up. Then there is the breaker in the electrical panel that feeds that disconnect to the ac unit.
On the unit, there should be a nameplate , usually made out of stamped metal but sometimes it's a decal and it will have a place that says FLA or FLC. This stand for full load amps or full load current (expressed as amps or amperes). The disconnect and the panel breaker feeding it should be sized at 125 %. Say, for example, the plate says 23 A for FLA. Then the disconnect and breaker should each be 30 A. The reason is two-fold. First, the start-up current, sometimes called locked rotor current. It takes more current to start a motor from a dead stop than it takes to keep running. Secondly, any device that might run for three hours or more is considered continuous duty and should take no more than 80 % of the current available from the breaker. The funny thing is 125% and 80% are reciprocal of each other. That is, 23 is 80 % of 30 and 30 is 125 % of 23. Also, the wire available should be sized to consider temperature derating considering temperatures it might be exposed to, derating by the temp range of the lugs they connect to. For example, at work, we choose wire size based on 60 degrees Celsius specs (about 149 F). The cheapest lugs one might find in equipment will be no less than that. Also, if the wire has to go a long distance from panel to disconnect and then to the unit, there might be a voltage drop though it should be minimal for about a 100 feet.
The interesting thing is that you said it was working fine with another breaker. Why was it inspected? For insurance purposes or did you have to get a permit for renovations?
Modern AC units will have two capacitors. A regular one that help runs and start the fan motor on the condenser. The second one is called a hard start cap and it is designed to take on a huge charge to help start that and the compressor itself. So, this may help hold down current surge on start up but I'm trying to think of how a smaller breaker would affect the operation of the unit without tripping.
Another question is, even though it's new, how often have you changed the filter in your central unit in the house? I've changed 3 times in two months. I have also just cleaned, after a few months from the previous time, the evaporator coils in the central unit. An ac guy I know on the project I'm at mention some special cleaning spray I can get at a supply house plus a small coil comb to help clean even better than the old toothbrush I have been using. Also, with kids and pets, you are likely to have a lot of dust and fur. So, you may need a cleaning of the evaporator coils. And, we are having daily highs of 100 F or more. During the hottest part of the day, about 102, it gets down to about 75 or 76 in the house but the unit stays running.
Plus, you can hose off dust on the outside unit where the condenser is (that radiator looking thing).
I'm just wondering if these other things have coincided with replacing the breaker with a smaller one. An inspector is likely to look at a breaker as too big if it is more than 125 % bigger than the FLA even though, in the code book, you can have percentages higher than that depending on the motor and duty rating.
When you say smaller breaker, do you mean physical size of the disconnect or less amperage?